Stuart Chignell wrote:
Is that what we would pay? I mean were you able to get it at that price because of the work you did your self?


I paid the usual retail price that anyone else would pay from an EV place in WA


Quote:
When you say "best done with PV panels" is this because sunlight is free or some other reason?


Operating a generator at 80%-> 5% isn't good for it, nor an efficient use of fuel. PV panels and a regulator will do it much better, and zero marginal cost. PV power is also much less expensive than diesel power, and vastly more environmentally friendly.
You are generally better off to oversize the PV array and not the battery- PV modules are a lot less expnsive than batteries, and an oversized array can help a lot in mostly cloudy weather.

Quote:
The system I'm working on at the moment needs about 1.5kW 24hrs per day but I want to design it so it can be scaled up to 5kW.


As a rough guess without calculating anything, for an off-grid system I reckon a 25kW PV array arranged as per my Virtual Tracker design and a 100kWh battery should mean minimal generator usage for most of the year in Victoria, to run 5kW of continuous load.


Quote:
The other challenge is the voltage to run the system at.



Dependent on what you are wanting to run... I'm happy with the performance of the pump I'm testing, it runs at a nominal battery voltage of 48V, but best max power performance is at 58.5V. The controller converts this to 3phase AC, and there are higher voltage versions available. What voltage would your air pumps be?


Top
 Profile  
Reply with quote  
    Advertisement
 
PostPosted: May 14th, '15, 17:25 
Seriously, this cant be healthy.
Seriously, this cant be healthy.
User avatar

Joined: Feb 23rd, '07, 03:48
Posts: 6715
Location: Lyonville Victoria
Gender: Male
Are you human?: yes
Location: Lyonville
Gunagulla wrote:
Stuart Chignell wrote:
Is that what we would pay? I mean were you able to get it at that price because of the work you did your self?


I paid the usual retail price that anyone else would pay from an EV place in WA

What about installation and associated costs?

Gunagulla wrote:
Quote:
When you say "best done with PV panels" is this because sunlight is free or some other reason?


Operating a generator at 80%-> 5% isn't good for it, nor an efficient use of fuel.

The system would be designed to run the generator at ~80% of capacity or not at all. I've been told that this is the point of peak fuel efficiency. In emergencies (battery failure or some other catasrophe) the generator could be run to power the system directly but this would be a last resort.

Quote:
PV panels and a regulator will do it much better, and zero marginal cost. PV power is also much less expensive than diesel power, and vastly more environmentally friendly.
You are generally better off to oversize the PV array and not the battery- PV modules are a lot less expnsive than batteries, and an oversized array can help a lot in mostly cloudy weather.

The problem is that to be confident you are never going to run short of power the PV panel array and the battery bank have to be relatively large. Since a generator is essential for redundancy it makes sense to have it integrated with the system.

If someone can show me that it is more cost effective to only have the generator for emergency backup and the PV panel array and battery bank 100% of primary power then I'd invest in that system.

Gunagulla wrote:
Quote:
The system I'm working on at the moment needs about 1.5kW 24hrs per day but I want to design it so it can be scaled up to 5kW.


As a rough guess without calculating anything, for an off-grid system I reckon a 25kW PV array arranged as per my Virtual Tracker design and a 100kWh battery should mean minimal generator usage for most of the year in Victoria, to run 5kW of continuous load.

Do you have a rough idea of how much that would cost?

Gunagulla wrote:
Quote:
The other challenge is the voltage to run the system at.


Dependent on what you are wanting to run... I'm happy with the performance of the pump I'm testing, it runs at a nominal battery voltage of 48V, but best max power performance is at 58.5V. The controller converts this to 3phase AC, and there are higher voltage versions available. What voltage would your air pumps be?


The water and air pumps are available "bare" as in you just get the pump without a motor to make it work. THat means I can put whatever motor I want on them from a tractor PTO to 3phase electric to DC. I have looked at DC motors so as to do away with an inverter (at least a large one anyway). The trouble there though is finding the right motor and getting a system to run at the right voltage. As I understand it low voltage systems need seriously fat cables to get enough power through them but high voltage DC systems are not so common so can't be just bought off the shelf.

The preliminary conclusion I came to was that it was better to run standard 3 phase kit because it was available off the shelf.


Top
 Profile  
Reply with quote  
PostPosted: May 14th, '15, 17:26 
Seriously, this cant be healthy.
Seriously, this cant be healthy.
User avatar

Joined: Feb 23rd, '07, 03:48
Posts: 6715
Location: Lyonville Victoria
Gender: Male
Are you human?: yes
Location: Lyonville
You were going to send me the details on that pump. What is it capable of? What are its efficiencies?


Top
 Profile  
Reply with quote  
PostPosted: May 14th, '15, 17:49 
A posting God
A posting God
User avatar

Joined: Mar 9th, '13, 10:44
Posts: 3455
Location: Loomberah NSW
Gender: Male
Are you human?: Im a force of nature
Location: I'm right here
I'm still working on that! I've only had it running a few days, but with only 5 beds connected I can only run at just above the minimum speed that will pump to 5m head. Once I get a few more beds ready and connected I'll be able to run it faster and do some efficiency tests etc. The 500W version I have will pump 15.3m^3 per hour at zero head, and there is a 900W 48V version, and a 1200W 72V version that pumps 27.9m^3/hr.
I'll send the brochure.


Top
 Profile  
Reply with quote  
PostPosted: May 14th, '15, 18:36 
A posting God
A posting God
User avatar

Joined: Mar 9th, '13, 10:44
Posts: 3455
Location: Loomberah NSW
Gender: Male
Are you human?: Im a force of nature
Location: I'm right here
Stuart Chignell wrote:
What about installation and associated costs?


I installed it myself, cabling etc costs would depend on the particular installation, so hard to put a number on that.


Quote:
The system would be designed to run the generator at ~80% of capacity or not at all.


We're only talking about a 6kW generator, which isn't very large. With a system as I described you wouldnt need to run it very often. I think the best way to convert 6kW @230V to your battery voltage would be via a welder transformer and large capacity rectifier.


Quote:
The problem is that to be confident you are never going to run short of power the PV panel array and the battery bank have to be relatively large. Since a generator is essential for redundancy it makes sense to have it integrated with the system.


Yes, and save money by not going overboard on battery capacity, it's just too expensive. Size it to minimise generator use, not eliminate it, based on BOM solar radiation data over a long period.


Quote:
If someone can show me that it is more cost effective to only have the generator for emergency backup and the PV panel array and battery bank 100% of primary power then I'd invest in that system.
Do you have a rough idea of how much that would cost?



Roughly- good quality panels such as Yingli can be had for $1.20/watt these days, 20kW = $24K Mounting depends on roof, and what sort, angle etc, or ground mount, but its going to be several thousand I would guess. LiFePO4 cells were going for about $1.80/AH last I saw, but would probably be less for a large quantity, so for 100kWh, say $50-60K. $5K for charge controllers, and perhaps another $3K for BMSs. Probably looking at close to $100K including installation.
Lower voltage equipment can easily be catered for with DC to DC converters.

There are DC motors around, but sourcing a large number of a particular voltage and various kW ratings may prove to be quite a challenge. However, the pump I have, or other varieties of it, may be suitable.

Re cabling- if you were talking about ~1kW motors, then at 50V you'd need cabling to carry 20A with minimal volt drop- 16mm^2 would be fine if your runs were ~20m. Of course you could arrange the systems to minimise cable runs- maybe radial layout with larger pumps near the centre.


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 06:32 
Almost divorced
Almost divorced

Joined: Oct 16th, '14, 08:44
Posts: 1253
Gender: Male
Are you human?: Mostly
Location: Orlando, FL USA
For someone only using batteries for a backup. Say in a tropical climate where hurricanes and Typhoons are possible. 3 to 6 days without power possible. Wouldn't it be more cost efficient to charge a battery bank with a trickle charger off mains power. That way you could bypass the need to buy solar panels and even a generator if you were willing to risk it. And the battery bank was sized properly.


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 06:42 
A posting God
A posting God
User avatar

Joined: Mar 9th, '13, 10:44
Posts: 3455
Location: Loomberah NSW
Gender: Male
Are you human?: Im a force of nature
Location: I'm right here
Solar panels are much less expensive than batteries. For off-grid domestic systems, oversizing the PV panels and not having a huge battery is the most economical way to do it. Having a huge battery capacity that gets used maybe once or twice per year wouldn't be the best way to go about it IMO.


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 07:07 
Almost divorced
Almost divorced

Joined: Oct 16th, '14, 08:44
Posts: 1253
Gender: Male
Are you human?: Mostly
Location: Orlando, FL USA
Thanks


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 07:30 
A posting God
A posting God
User avatar

Joined: Mar 9th, '13, 10:44
Posts: 3455
Location: Loomberah NSW
Gender: Male
Are you human?: Im a force of nature
Location: I'm right here
If you were going to use a battery purely for backup, one of the gel cells that claims 400 cycles of running to flat would be the way to go- that way you don't have to worry so much about very deep discharges, which will damage most batteries. I'd give it a top up charge ~once per month, or just before nasty weather is forecast, rather than have it trickle charging all the time though.


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 08:21 
Seriously, this cant be healthy.
Seriously, this cant be healthy.
User avatar

Joined: Feb 23rd, '07, 03:48
Posts: 6715
Location: Lyonville Victoria
Gender: Male
Are you human?: yes
Location: Lyonville
Gunagulla wrote:
Stuart Chignell wrote:
What about installation and associated costs?


I installed it myself, cabling etc costs would depend on the particular installation, so hard to put a number on that.

That makes a big difference to the costs. For something like this because it is so crucial I'd want someone else to do the work. There are only so many things I can do myself :(

Gunagulla wrote:
Stuart Chignell wrote:
The system would be designed to run the generator at ~80% of capacity or not at all.


We're only talking about a 6kW generator, which isn't very large. With a system as I described you wouldnt need to run it very often. I think the best way to convert 6kW @230V to your battery voltage would be via a welder transformer and large capacity rectifier.

Ok so now I'm confused again. Didn't you say that your ~20kWh battery bank could be charged in about an hour? Assuming its from 50% charge at a rate of 1C a 25kW generator running at 80% would take 1/2 an hour to top the batteries off.

Is this right or have I missed something?


Gunagulla wrote:
Stuart Chignell wrote:
Quote:
The problem is that to be confident you are never going to run short of power the PV panel array and the battery bank have to be relatively large. Since a generator is essential for redundancy it makes sense to have it integrated with the system.


Yes, and save money by not going overboard on battery capacity, it's just too expensive. Size it to minimise generator use, not eliminate it, based on BOM solar radiation data over a long period.

I probably would aim to moderate generator use rather than minimise it. Slight but significant difference.

Gunagulla wrote:
Stuart Chignell wrote:
If someone can show me that it is more cost effective to only have the generator for emergency backup and the PV panel array and battery bank 100% of primary power then I'd invest in that system.
Do you have a rough idea of how much that would cost?



Roughly- good quality panels such as Yingli can be had for $1.20/watt these days, 20kW = $24K Mounting depends on roof, and what sort, angle etc, or ground mount, but its going to be several thousand I would guess. LiFePO4 cells were going for about $1.80/AH last I saw, but would probably be less for a large quantity, so for 100kWh, say $50-60K. $5K for charge controllers, and perhaps another $3K for BMSs. Probably looking at close to $100K including installation.

And again this is where I am confused. Why so large a battery bank? 100kWh would run the system on batteries alone for say 10hrs to 50% discharge. Such a large battery would certainly moderate the amount of time the generator was needed but that is a huge capital outlay for the batteries.

While diesel costs more and is less environmentally friendly the depreciated cost of the batteries would be pretty significant.

Plus one of the biggest issues is lack of startup capital. While a larger battery bank may save me money in the long run it is going to be more important to generate more production even if that production has a higher cost of production with diesel than with solar via batteries. Later as we get past the first harvest we can add more batteries to reduce the reliance on diesel.

That begs the question of how small a bank can I go.

Gunagulla wrote:
Lower voltage equipment can easily be catered for with DC to DC converters.

There are DC motors around, but sourcing a large number of a particular voltage and various kW ratings may prove to be quite a challenge. However, the pump I have, or other varieties of it, may be suitable.

As discussed I am concerned about the efficiencies but I am used to looking at these things in terms of $/kWhr. If most of our electricity is coming from PV it changes things a bit. A more efficient pump will need less panels to run it and less battery bank but I am not sure how the numbers stack up. When doing comparisons based on cost of electricty per kWH I have a spread sheet that tells me how much efficiency changes the delivered cost of electricity and how quickly a more efficient pump pays for itself.


Gunagulla wrote:
Re cabling- if you were talking about ~1kW motors, then at 50V you'd need cabling to carry 20A with minimal volt drop- 16mm^2 would be fine if your runs were ~20m. Of course you could arrange the systems to minimise cable runs- maybe radial layout with larger pumps near the centre.

Yeah good idea.


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 11:40 
A posting God
A posting God
User avatar

Joined: Mar 9th, '13, 10:44
Posts: 3455
Location: Loomberah NSW
Gender: Male
Are you human?: Im a force of nature
Location: I'm right here
Stuart Chignell wrote:
Ok so now I'm confused again. Didn't you say that your ~20kWh battery bank could be charged in about an hour? Assuming its from 50% charge at a rate of 1C a 25kW generator running at 80% would take 1/2 an hour to top the batteries off.


Yes I did, but I hate generators and don't have one myself ;) However, you were talking about running a 5kW system from a generator, so you'd only want a ~6kW generator to run a 5kW system, not a 20kW generator running at 25% capacity.


Quote:
And again this is where I am confused. Why so large a battery bank? 100kWh would run the system on batteries alone for say 10hrs to 50% discharge.


So you dont have to listen to the generator and pay for fuel for days on end in winter.
If you put in a 20kWh battery, you'll only get 3 hours use from it, so lots of generator starts overnight. What if something breaks in the genny at 9pm and you cant get the replacement part needed to start it until 9am or 2 days later if it happens on Friday night- lots of dead fish is what happens!


You should be able to lease batteries in the not too distant future- zero capital outlay. You can lease PV panels & inverters now for zero outlay for grid-connected systems. My Employer, SunEdison, does 24hour monitoring on their leased grid-connected systems, so they'd know in near real time if say an inverter decided to pop.

I'd think seriously about a leased grid-connected solar system to start, with battery backup for blackouts, and a diesel generator as a backup to the backup if the outage lasts too long. I'd be happy with 20kWh of battery in that case. You would only need a 6kW generator and would rarely need to use it. Buy 100% green power for your grid imports!


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 12:01 
Seriously, this cant be healthy.
Seriously, this cant be healthy.
User avatar

Joined: Feb 23rd, '07, 03:48
Posts: 6715
Location: Lyonville Victoria
Gender: Male
Are you human?: yes
Location: Lyonville
Gunagulla wrote:
Stuart Chignell wrote:
I'd think seriously about a leased grid-connected solar system to start, with battery backup for blackouts, and a diesel generator as a backup to the backup if the outage lasts too long. I'd be happy with 20kWh of battery in that case. You would only need a 6kW generator and would rarely need to use it. Buy 100% green power for your grid imports!


I think this is going to be the way to go. Rules out a bunch of sites but such is life. My only concern would be power companies objecting to solar installation and/or attempting to add surcharges for solar connections.


Top
 Profile  
Reply with quote  
PostPosted: May 15th, '15, 12:31 
A posting God
A posting God
User avatar

Joined: Mar 9th, '13, 10:44
Posts: 3455
Location: Loomberah NSW
Gender: Male
Are you human?: Im a force of nature
Location: I'm right here
We (well my work, not me personally) often do zero export installations- the power companies dont like solar, often because it messes with their undersized transformers and wires.

You might be interested in this: http://reneweconomy.com.au/2015/trina-s ... rage-31674


Top
 Profile  
Reply with quote  
PostPosted: May 22nd, '15, 18:54 
Seriously, this cant be healthy.
Seriously, this cant be healthy.
User avatar

Joined: Feb 23rd, '07, 03:48
Posts: 6715
Location: Lyonville Victoria
Gender: Male
Are you human?: yes
Location: Lyonville
Article really argues that it would be a good idea to minimise the money you spend on batteries.

http://rameznaam.com/2014/10/05/solar-wind-plunging-below-fossil-fuel-prices/


Top
 Profile  
Reply with quote  
PostPosted: May 22nd, '15, 21:24 
A posting God
A posting God
User avatar

Joined: Jul 6th, '14, 20:25
Posts: 3854
Location: 2.2 kilometers up, NM, USA
Gender: Male
Are you human?: Series of particles
Location: Sapello, New Mexico USA
How's it going with the Li-Ion batteries? Have you chosen a particular battery to test yet?
Attachment:
Li-Ion-battery.jpg
Li-Ion-battery.jpg [ 124.64 KiB | Viewed 6223 times ]

http://www.homepower.com/articles/solar-electricity/equipment-products/lithium-ion-batteries-grid-systems
I don't know much about them. Your post has me thinking more and more about Li-Ion as a storage call for my pumps.


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 30 posts ]  Go to page Previous  1, 2

All times are UTC + 8 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  

Powered by phpBB® Forum Software © phpBB Group
Portal by phpBB3 Portal © phpBB Türkiye
[ Time : 0.103s | 16 Queries | GZIP : Off ]