 Post subject: Re: Recycled UPS
PostPosted: Jan 13th, '12, 10:01 
Almost divorced
Almost divorced
User avatar

Joined: Nov 11th, '09, 03:13
Posts: 1004
Gender: Male
Are you human?: The top half is
Location: Chiang Mai, NW Thailand.
My head a little clearer this morning...
The 420 Watts (In Jaymie's unit) is the Power Factor adjusted value (Power factor of computer equipment is around 70%) and nothing to do with battery capacity, in fact on the APC website they don't specify the battery capacity anywhere.
So that was a bad example.

My estimate of 72 hours for your system is wrong too, more like 50 hours (70%)
It will depend on the power factor of your pump.

So to re-answer your question "How long will it last?"

I have no idea, plug it in and try it :D


Top
 Profile  
Reply with quote  
    Advertisement
 
 Post subject: Re: Recycled UPS
PostPosted: Jan 13th, '12, 10:43 
A posting God
A posting God
User avatar

Joined: Oct 16th, '11, 06:12
Posts: 2019
Gender: Male
Are you human?: 0110010110
Location: Brisbane, qld
Unfortunately I'm not sure if there is an easy way to explain power factor.
So if you are really in the mood for thinking .. ask DuiNui :D

I don't feel like thinking about it enough to explain it in an easy to understand way, sorry :whistle:


Top
 Profile  
Reply with quote  
 Post subject: Re: Recycled UPS
PostPosted: Jan 13th, '12, 12:58 
Newbie
Newbie
User avatar

Joined: Jul 17th, '09, 03:21
Posts: 16
Gender: Male
Location: Olathe, Kansas, USA
In an AC circuit there is an "apparent" power and a "real" power. The apparent power is proportional to the current times the voltage. The real power (or the actual work being done), is the apparent power times the power factor. The power factor is related to the phase shift between between the voltage and the current. Theoretically a resistive load like a heating element will have no phase shift and the power factor will be 1. Inductive loads such as transformers and motors will cause a phase shift between the current and voltage that will cause the apparent power to be greater than the actual work being done. The adjustment from the apparent power to the real power is the power factor which is the cosine of the phase angle between the current and the voltage.
Think of it as a freshly poured glass of beer. The volume of the full glass is the apparent power. The real power is the liquid in the glass doing all the work, and the power factor determines how much of a head you have on the glass.
At least that's my understanding anyway. My background is not electrical.


Top
 Profile  
Reply with quote  
 Post subject: Re: Recycled UPS
PostPosted: Jan 13th, '12, 13:21 
Almost divorced
Almost divorced
User avatar

Joined: Nov 11th, '09, 03:13
Posts: 1004
Gender: Male
Are you human?: The top half is
Location: Chiang Mai, NW Thailand.
I haven't done this stuff since school, I try to stay away from AC stuff, it's nasty and makes my head hurt.

As you're thinking about doing an ultra low power thing BW, you might want to look into power factor correction.
This site explains it quite nicely.
http://www.allaboutcircuits.com/vol_2/chpt_11/4.html

Basically you want to put a cap across your pump power to try to cancel out the effects of an inductive load (the motor), make sure the cap is rated for mains :D

But with a 200Ah battery and an 8W pump, it's probably not worth the trouble tbh.


Top
 Profile  
Reply with quote  
 Post subject: Re: Recycled UPS
PostPosted: Jan 13th, '12, 14:35 
A posting God
A posting God
User avatar

Joined: Oct 16th, '11, 06:12
Posts: 2019
Gender: Male
Are you human?: 0110010110
Location: Brisbane, qld
@IMelting: Now you have to explain phasors and why inductive loads cause the current to lag with respect to the voltage, and how a capacitor does the opposite :funny1:


Top
 Profile  
Reply with quote  
 Post subject: Re: Recycled UPS
PostPosted: Jan 14th, '12, 13:11 
Seriously, this cant be healthy.
Seriously, this cant be healthy.
User avatar

Joined: Mar 26th, '10, 20:46
Posts: 5404
Location: South Australia
Gender: Male
Are you human?: Yep
Location: South Australia
Woah. Thanks power factor people. A lot to learn about everything.


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 66 posts ]  Go to page Previous  1, 2, 3, 4, 5

All times are UTC + 8 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  

Powered by phpBB® Forum Software © phpBB Group
Portal by phpBB3 Portal © phpBB Türkiye
[ Time : 0.031s | 13 Queries | GZIP : Off ]